An electric heater calibrated $$1.5\,kW, 230\,V$$ is connected to a household branch circuit having $$5$$ A fuse wire and is, made to work. What will happen?

Solution
Verified by Toppr

Given,
The power rating of the electric heater, $$P=1.5\ kW=1500\ W$$
Voltage, $$V=230\ V$$
Safe current rating of fuse wire, $$I_{safe}=5\ A$$

We know,
$$P=VI$$

$$\implies I = \dfrac PV$$

$$\implies I = \dfrac {1500}{230}$$

$$I=6.52\ A$$

$$I\gt I_{fuse}$$
$$\therefore the fuse wire will burn$$

Was this answer helpful?
5
Similar Questions
Q1
An electric heater calibrated $$1.5\,kW, 230\,V$$ is connected to a household branch circuit having $$5$$ A fuse wire and is, made to work. What will happen?
View Solution
Q2
An electric iron calibrated 1.5 kW, 230 V is connected to a household branch circuit having 5 A fuse wire and is made to work. What will happen?
\( 9= \)
View Solution
Q3
In a household electric circuit different appliances are connected in parallel to one another. Give two reasons. An electrician puts a fuse of rating 5A is that part of domestic electric circuit in which an electrical heater of rating 1.5 kW,220 V is operating. What is likely to happen in this case and why? What is likely to happen in this case and why?